  3. M0117 ESC rough control
esc
47 Posts 3 Posters 26.3k Views 2 Watching
    @Aaky , thank you for providing the details. Actually, I do have this exact propeller, so I will be able to help you very soon.
    I will recommend to leave the kp and ki parameters disabled until you have a stable flight. Having aggressive response in ESC is not always a good thing, especially if you have a lot of gyro noise, so it's best to start with a soft ESC response and experiment with higher gains later.
    Let me get back to you after the weekend. Meanwhile, please read this document carefully and go through the tuning procedure : https://gitlab.com/voxl-public/voxl-sdk/utilities/voxl-esc/-/blob/master/voxl-esc-tools/calibration.md . Leave the kp and ki terms zero for now.
    For spinup params, please try these:
        <param name="spinup_type"         value="1"/>      <!-- 0: traditional, 1: sinusoidal -->
        <param name="spinup_power"        value="120"/>     <!-- power used to during spin-up procedure -->
        <param name="latch_power"         value="80"/>     <!-- power used during latching stage of spin-up (out of 999)-->
        <param name="spinup_power_ramp"   value="8"/>      <!-- it will take ( 4096 / (spinup_power_ramp*10000) ) seconds to ramp sinusoidal start-up power from 0 to spinup_power -->
        <param name="spinup_rpm_target"   value="2000"/>   <!-- Desired RPM at the end of the sinusoidal spin-up procedure -->
        <param name="spinup_time_ms"      value="1000"/>   <!-- Duration of the sinusoidal spin-up procedure -->
        <param name="spinup_bemf_comp"    value="1"/>      <!-- 0: disable, 1:enable back-emf compensation in sinusoidal spin-up procedure -->
        <param name="motor_kv"            value="1500"/>   <!-- kV value of the motor. used in back-emf compensation during spin-up -->
    spinup_rpm_target you could set more accurately to the value that your motor+prop spin at about 10% power (you can test this using voxl-esc-spin.py test command). This way, the target RPM of the spinup procedure will be roughly the idle RPM at minimum power.
    Also, please double check your PX4 tuning parameters and make sure they have not changed from the last time you had good flight.
    Aaky
    @Alex-Kushleyev Sure Thanks Alex. Will follow this procedure for our current tests. Regarding calibration part, We generally do something like putting propeller in reverse direction where air is pushed upwards and not downwards and then run voxl-esc-calibration script. This also should yield good results for a0,a1 and a2 parameters to be derived?
    A 1 Reply Last reply
    • A Aaky
      Aaky
      @Alex-Kushleyev Following up over my query. If you have good tune and how you achieved it with the above mentioned motor and propeller set, please let me know.
      • A Aaky
        @Aaky , yes, sorry for the delay. I have been working on this and should have an update for you this evening with a parameter file and some plots.
          #10
          @Aaky , I just posted the ESC param file here :
          • https://gitlab.com/voxl-public/voxl-sdk/utilities/voxl-esc/-/blob/dev/voxl-esc-params/misc/esc_params_tm_2203_5_1500kv_6042_3.xml -- all my final recommended settings are in this file, below you will find some explanations.
          I used the latest ESC firmware for M0117 ESC :
          • https://gitlab.com/voxl-public/voxl-sdk/utilities/voxl-esc/-/blob/dev/voxl-esc-tools/firmware/modalai_esc_firmware_m0117_1_v0_39_RC10_eb6fb500.bin
          All tests were performed on a ID 0 of the 4-in-1 ESC.
          Calibrations results are nice and smooth:
          ./voxl-esc-calibrate.py --id 0
          Feed forward params from calibration:
              <param name="pwm_vs_rpm_curve_a0" value="338.4975"/>
              <param name="pwm_vs_rpm_curve_a1" value="0.51777"/>
              <param name="pwm_vs_rpm_curve_a2" value="3.56026e-05"/>
          Ramp from 10 to 100% power at full battery (16.5V) - also nice and smooth.
          ./voxl-esc-spin.py --id 0 --power 100 --ramp-time 2.0 --timeout 3.5 --init-cmd 10 --init-time 1.0 --cmd-rate 2000 --enable-plot 1
          Maximum RPM (I set 15K in ESC params as absolute max), you may want to limit in PX4 because at discharged battery, 15K rpm cannot be achieved
          • 13800 RPM @ 14.2V, 14.7A
          • 14900 RPM @ 16.1V, 17.5A
          I set the sinusoidal spin-up params to target 2000 rpm (which is about the minimum rpm at 10% power) and it will take 1 second to spin up. If you want to spin up faster if you can do that and maybe also increase the spinup_power from 110 to 130 if you choose faster spinup. Sometimes, spinning up too fast at lower power can loose sync.
          protection_stall_check_rpm param has been set to 1000RPM which is half of the minimum RPM.
          Step tests using the following command (running on PC, so high command rate for more data):
          ./voxl-esc-spin-step.py --id 0 --init-time 1.0 --init-cmd 3000 --rpm 3000 --step-amplitude 4000 --timeout 3.0 --enable-plot 1 --cmd-rate 2000
          • RED : kp = 0, ki = 0 (only feed-forward term is enabled)
          • GREEN : kp = 50, ki = 5, max_kpe = 100, max_kie = 50
          • BLUE : kp = 100, ki = 15, max_kpe = 200, max_kie = 100
          • Interpretation of this plot:
            • RPM response of RED plot (kp,ki = 0) is considerably slower than others
            • with kp = 50 and kp = 100, you see significantly larger current spikes during the upward transition
            • kp=50 is significantly faster than kp=0, but kp=100 is not much faster than kp=50, although uses noticeably more current, which may mean that the motor torque saturates and not able to produce higher torque with higher current.
          The final configuration (as committed), i suggest the following. If you want softer response, you can drop kp and ki to zero and work on PX4 tuning, and then later if you want faster ESC response, set back to these. Please note that if you have a lot of gyro noise, it will result in noisy RPM commands and aggressive ESC response will try to track noisy RPM commands and can make the vehicle shake and make things worse. I would not say that my final params are too "aggressive", but the response is pretty fast and very smooth. The rest depends on your PX4 params and gyro noise 🙂
              <param name="kp"                  value="50"/>    <!-- RPM controller proportional gain -->
              <param name="ki"                  value="5"/>     <!-- RPM controller proportional gain -->
              <param name="max_kpe"             value="100"/>    <!-- maximum proportional erorr term (max is 999) -->
              <param name="max_kie"             value="50"/>     <!-- maximum integral error term (max is 999) -->
              <param name="max_rpm_delta"       value="8000"/>    <!-- cap for maximum rpm error used in RPM controller -->
          Two final recommendations:
          • keep an eye of ESC temperature (which is saved in PX4 logs). it helps to review the temps after first few flights to make sure they are staying in the <80 C range. (100C+ would be too high), 50-60 is ideal. You can try to keep the ESC open to the air flow from the propellers and should be OK.
          • You may consider adding an electrolytic capacitor to the ESC power pads if you are going to try aggressive flights, it should help keep the ESC performance smooth.
          Please let me know if you have any more questions.
            Aaky
            @Alex-Kushleyev Thanks Alex for such a detailed response and explanation. I will flash the parameters and check the response in flight and get back to you over this. Thank you once again!
            • A Aaky
              #12
              @Aaky , you are welcome. Also, i wanted to note that i have tested these params in very extreme case where rpm steps are between 2000 and 15000 rpm (worst case scenario) using the following command:
              ./voxl-esc-spin-step.py --id 0 --init-time 1.0 --init-cmd 2000 --rpm 2000 --step-amplitude 13000 --timeout 3.0 --enable-plot 1
              The response was stable, see the plot below. Obviously very high current, reaching 40A during peak (for just a single motor).
              Also, you asked about running the ESC calibration with propeller reversed (blowing air down). It is an interesting idea and it should work, but I do not recommend it due to safety reasons. When I run the calibration, the motor is always rigidly attached to a solid structure, whether it is just a standalone arm with just one motor / prop or if I am using the whole drone, i find a way to mechanically fix it to a work bench or something heavy (depending on circumstances). Also being close to the ground, calibration could be slightly affected by the ground effect / high air disturbance, but the main factor to consider is safety.
              2000-15000 RPM Step Results:
                Aaky
                @Alex-Kushleyev Thanks Alex. Graphs look good. I am yet to stress test with these parameters but I was able to takeoff my drone with these parameters and it seemed to be very smooth. Will perform more tests in upcoming days and get back to you.
                • A Aaky
                  Aaky
                  wrote on last edited by Aaky
                  #14
                  @Alex-Kushleyev I had one general query. I am using in one of my drone VOXL2 IO with Tmotor ESC with recent Oneshot Build which you shared with me previously.
                  Below are my queries.
                  1. If I want to compare VOXL2 ESC 4 in 1 with VOXL2 IO + Tmotor ESC setup what would yield better results? I understand we have some closed loop control with VOXL2 4-in-1 ESC as compared to VOXL2 IO based setup but is this closed loop control actually functional in flight and more better for aircraft under 3 kg weight category? Also is there a way to loop back ESC telemetry from Tmotor like ESC to PX4 on any of its UART ports with voxl-px4 firmware? Can that help apart from diagnostics?
                  2. I have worked with Arducopter firmware where ESC telemetry helps to identify and track harmonic notches improving overall tuning results, have you heard of anything like that in PX4? (This is PX4 specific query I understand but just wanted to check if I can do any better with Tmotor like ESC providing telemetry back to PX4)
                  3. Does VOXL ESC controls motors in closed loop by detecting RPM/Power while PX4 is commanding drone in Position flight mode?
                  • A Aaky
                    @Aaky , Please see below answers to your questions
                    1. Whenever you are using any of the VOXL ESCs in PX4, they are always doing closed-loop RPM control. The ESCs themselves are capable of operating on "open loop" mode, similar to traditional ESCs and that can be tested using voxl-esc tools (we refer to it as power control as opposed to rpm control. The RPM closed loop control is always active in flight. We do not support telemetry using VOXL2 IO board - if you want detailed telemetry from ESCs, you should use ModalAI ESCs, which provide, voltage, current, rpm, esc temperature, applied % power, each at 200Hz (while flight control loop is running at 800hz). This data is already available and being logged to px4 logs (although not at such a high rate, which could be modified on the px4 side). The ESC information is published via esc_status topic.
                    Closed loop control, when tuned properly, provides superior (over open loop) behavior and that is why we use it. Not only the control is accurate, it is also generally faster (depending on your PI gains in ESC params). The speed of ESC response becomes more important as vehicle gets smaller - this is because smaller vehicles have faster dynamics and can benefit more from faster motor response. With large vehicles, their large moment of inertia may prevent fast ESCs from providing any benefit. I already shared some plots above in this thread that show you how much difference in response time the proportional control can make.
                    1. I am not sure about PX4 features that track "harmonic notches improving overall tuning results". However, the ModalAI ESC does RPM control and provides RPM feedback, so this information can be used for filtering out vibrations (I believe that this is what you are referring to). Beyond this, I cannot provide any more guidance as we have not used such features in PX4.
                    2. In all flight modes, if you use ModalAI ESC with PX4, closed loop RPM control is used.
                    If I were to summarize the benefit of closed loop ESC control vs closed loop RPM control in one statement, it would be something like this.. For small vehicles, in absence of excessive vibrations, the faster closed loop RPM control should allow you to increase your attitude control (roll, pitch, yaw) gains in your flight controller (PX4), which means you can achieve more accurate flight.
                    If you have more questions, please let me know.
                      Aaky
                      #16
                      @Alex-Kushleyev Thanks for detailed response Alex. I am currently using this ESC from Tmotor. This ESC is running with BLHeli32 firmware. Any idea if this has closed loop RPM control? Since this ESC provides telemetry feedback I am guessing it has some closed loop control but I dont know if I can tune its response with any PI parameters as that of VOXL ESC. Let me know if you have any information.
                      Reason behind all these queries is I have custom drone with VOXL2 IO and above shown Tmotor ESC. I have tried manual and Autotuning the aircraft, well it flies but while I fly it in indoors it dosent seem to be accurately holding its posiiton and keeps moving around 10-15 cms in horizontal axis. Also the yaw control is not very stable and aircraft wobbles in the interim mildly and again becomes stable. I am just checking is improving ESC going to solve my problems.
                      • A Aaky
                        @Aaky , as far as I know, BLHeli32 does not do closed loop RPM control, however it can report the RPM feedback (similar to how VOXL ESC is doing). the DShot protocol supports requesting telemetry, which is sent back to the flight controller via UART. In this configuration, there are 4 Dshot signals going from the flight controller and 1 UART TX coming back from the ESC into the Flight controller.
                        There is also a different telemetry option, where the ESC sends back telemetry sign the dedicated PWM / Dshot wires (same wires used to send Dshot commands from FC to ESC are used by ESC to send telemetry back to FC). The latter is called "dshot telemetry" and it can be sent at a much higher rate because each ESC has a dedicated signal line.
                        I believe Betaflight and maybe Arducopter can the Dshot telemetry for tracking what RPMs the motors are spinning and apply dynamic notch filters to try to filter out vibrations that are coming from all 4 motors.
                        You can find more information about dshot and telemetry here : https://brushlesswhoop.com/dshot-and-bidirectional-dshot/
                        What I would recommend, if it is possible for you, keep the current drone with VOXL2 IO and tmotor ESC and build another (identical) drone with the ModalAI ESC. Then you can test them side by side and compare flight performance with similar FC tuning and everything else being the same. It will be faster than swapping ESCs between the tests.
                          Aaky
                          #18
                          @Alex-Kushleyev Thanks Alex for alll the details. I will look into the test setup. What is the maximum continous current limit for this VOXL ESC? We have this ESC but not sure if it can replace Tmotor ESC specified in above link. Also what is maximum continuous current supported by this voxl esc? It is written 10A but upto what limits it is tested in miminal airflow conditions?
                          • A Aaky
                            Aaky
                            @Alex-Kushleyev Additionally,
                            Few stats from our motor : Our motor at hover time consumes 7.6 Amp and motor's peak current is at 18A. Current eventually increases as battery voltage decreases pushing hover current to 11A per motor.
                            Can this requirements be met with VOXL ESC 4-in-1 as linked above?
                            • A Aaky
                              @Aaky , what is the voltage? 4S or 6S?
                              M0117 s M0134 escs can handle more than 10A continuous but with proper cooling. It has to be tested in your conditions to be sure. Monitor the esc temperature and stop the test immediately if esc temp gets above 100-110 C. Ideally, esc should be in the 50-80C range.
                              If you have an M01117 already, you could use that for testing if voltage is 4s or lower.
                              Also it seems your motor power may be a bit insufficient, if at hover you could have 11A at low battery, but absolute max current is 18A (i assume charged battery). The motor may be operating with little margin (low thrust to weight ratio of the drone). Please check!
                                #21
                                Honestly, if you are building an fast quadrotor (fpv or similar) i would suggest using our FPV ESC, but if you want to give your M0117 a try, i can help you evaluate it and make sure it does not overheat during flight (the ESC temperature is reported from each ESC channel to PX4 and we also have optional warnings you can set if ESC temperature is too high / close to overheating).
                                  Aaky
                                  #22
                                  @Alex-Kushleyev Our voltage is 4S, compatible with M0117 but the challenge is in our design its extremely difficult to provide direct airflow to the ESC. So my worry is for 10+ Amp of continous current needs will ESC be able to provide that much. Also we are building a aircraft which is under 3 kg category and not an FPV for sure but at the same time we want it to fly in outdoor and indoor situations. We are using 10-11 inch propeller and aircraft diameter is around 55 cms. We want it to fly fast for sure due to customer needs.
                                  • A Aaky
                                    #23
                                    @Aaky , If there is any doubt, you should just go with the FPV ESC, which is currently our highest performing ESC (in terms of current capacity). The FPV ESC also includes power regulator for VOXL2, so you would not need the APM.
                                    I actually have a plot from a test we did using the FPV ESC. The test was run 4 motors about 9-10A each (39A total) for 90 seconds with ZERO cooling. What I mean by zero cooling, the ESC was placed 1 meter away from the motors behind a closed door to ensure there was absolutely no airflow coming from the propellers. So the ESC could only sink heat via motor wires and by radiation. This is a very tough test condition for the ESC. Ambient temperature was about 20C, which is not too high.
                                    Please note in temperature plot, there are two sets of temperature (bands). This is because two of the reported temperatures are coming from temperature sensors inside MCU (which show higher temp) and two temperatures are measured by dedicated temperature sensors next to mosfets (which show lower temp). MCU runs a little bit hotter because it generates internal heat by itself inside its package.
                                    90 sec, 39A, no cooling. temperature reached 91-98C
                                    another test: 120 sec, 23A total, no cooling. Temperature reached 66-72C
                                    So the first test is actually very close to your scenario, except it is using 6S battery. With 4S, the amount of heat will be much lower, because the heat in ESC is not linear with voltage (but worse, maybe quadratic). You can understand, that if you do not provide any cooling, the heat has nowhere to go and temperature will rise. The FPV ESC also has a larger PCB and more copper (compared to other ESCs), so it will take longer for temperature to rise.
                                    Even in the worse case scenario that you still need to cool down the ESC, you could make a heat spreader, which should help.
                                    One final note, i should add that the FPV ESC only has total current sensing, not individual ESC channel, like M0117 or M0134.
                                      Aaky
                                      @Alex-Kushleyev Noted Alex. Thanks for all the details. I have time constraints at the moment to procure and then deploy FPV ESC on our UAV so was trying to see if anything which is available with me can suffice the needs.
                                      • A Aaky
                                        Aaky
                                        @Alex-Kushleyev One quick query on VOXL2 IO board, According to this diagram is there a inverter present on VOXL2 IO board for S.BUS port? Say I have non inverted S.BUS packets coming to input of VOXL2 IO J3, will they be inverted by VOXL2 IO board?
                                        • A Aaky
                                          Aaky
                                          More details about my setup, I am trying to send S.BUS signals from my Transmitter via Doodle labs serial port and on UAV side, receiving the serial packets from Doodle labs modem and then feeding them into VOXL2 IO board. I do not have inverter for converting inverted UART to normal UART on Doodle labs with GCS side which I am planning to insert but will I need inverter for back converting normal UART to inverted UART on UAV side before feeding into VOXL2 IO or not is the question.